4specs.com    4specs.com Home Page

Smoke and Draft Control - UL 1784 Log Out | Topics | Search
Moderators | Register | Edit Profile

4specs Discussion Forum » Archive - Product Discussions #5 » Smoke and Draft Control - UL 1784 « Previous Next »

Author Message
Russ Hinkle, AIA, CDT, LEED AP
Senior Member
Username: rhinkle

Post Number: 107
Registered: 02-2006


Posted on Friday, December 21, 2012 - 10:22 am:   Edit PostDelete PostPrint Post

For most door and frame assemblies is the only way to meet IBC 715.4.3.1 to add smoke seals to the sides and head? I am trying to confirm what I have found on-line and what the hardware consultant is telling me.
Russ Hinkle
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1067
Registered: 03-2003


Posted on Friday, December 21, 2012 - 10:43 am:   Edit PostDelete PostPrint Post

Not exactly. The door and frame must be labeled as a smoke assembly, which is identified with an "S" on the label. Reference Section 715.4.6.3 (2009 IBC) or Section 716.5.7.3 (2012 IBC).
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
Russ Hinkle, AIA, CDT, LEED BD+C
Senior Member
Username: rhinkle

Post Number: 108
Registered: 02-2006


Posted on Friday, December 21, 2012 - 10:53 am:   Edit PostDelete PostPrint Post

So if the door and frame have the "S" on the label, then it meets the requirements of UL 1784, with or without seals.

HC tells me can't do it without seals (either added at the factory or in the field).
Russ Hinkle
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1068
Registered: 03-2003


Posted on Friday, December 21, 2012 - 11:06 am:   Edit PostDelete PostPrint Post

Seals are still required, but the door and frame must have been tested with seals, unless it passed without them, which I believe is nearly impossible. Some doors are provided with their own seals.
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
ken hercenberg
Senior Member
Username: khercenberg

Post Number: 394
Registered: 12-2006


Posted on Friday, December 21, 2012 - 11:06 am:   Edit PostDelete PostPrint Post

My guess is that to meet the S label requirements smoke seals are required. Since the label requires a tested assembly I'm not sure how field applied seals will work. If they are designed as part of the tested assembly to be field installed I presume it's a possibility.

We should probably reach out to George Everding for this one.
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1069
Registered: 03-2003


Posted on Friday, December 21, 2012 - 11:28 am:   Edit PostDelete PostPrint Post

UL 1784 isn't specific about the test samples. The standard is used to test complete door assemblies or gasketing systems for specific door assemblies.

Therefore, the door and frame assembly is tested either with integral seals or field-applied seals. If field-applied seals are used, the manufacturer may provide the seals with the door and frame for field application after field finishing, or the use of approved seals that have passed UL 1784 as a gasketing system.
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
Russ Hinkle, AIA, CDT, LEED BD+C
Senior Member
Username: rhinkle

Post Number: 109
Registered: 02-2006


Posted on Friday, December 21, 2012 - 01:16 pm:   Edit PostDelete PostPrint Post

So far I understand and it makes sense. What is peoples experience with a pair of doors? Is a seal typically needed at the 1/8" gap between the two doors? I am being told that typically the door bottom does not need to be sealed to pass the UL 1784 test.
Russ Hinkle
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1070
Registered: 03-2003


Posted on Friday, December 21, 2012 - 01:40 pm:   Edit PostDelete PostPrint Post

Bottom seals are not required, but a seal between a pair of doors is required.
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
John Bunzick, CCS, CCCA, LEED AP
Senior Member
Username: bunzick

Post Number: 1470
Registered: 03-2002
Posted on Friday, December 21, 2012 - 04:37 pm:   Edit PostDelete PostPrint Post

I think those steel doors that are welded shut pass, provided the welds are continuous. They can't be used in an egress path, however.
George A. Everding, AIA, CSI, CCS, CCCA
Senior Member
Username: geverding

Post Number: 646
Registered: 11-2004


Posted on Friday, December 21, 2012 - 04:52 pm:   Edit PostDelete PostPrint Post

I agree with the discussion. This issue has come up with some of the architects I work with as a door hardware consultant, and a while back I put together a response to one of them, slightly edited and quoted here. Ron, if you would, check the accuracy of my interpretation of code. And Ken, thanks for the email tip to visit this discussion. Happy Holidays to all:

It’s more complex than it needs to be – the code sends us on a bit of a chase to track things down. As you state, 2009 IBC Section 715.4.3.1 requires fire door assemblies to meet UL 1784 smoke and draft control requirements. There is nothing specific in either reference about gasketing – where and when it is required or what type it needs to be. IBC requirements are performance based: 3.0 cfm/sf of door opening at 0.10” H2O. In theory, a door assembly could pass UL 1784 with NO gasketing at all, but in reality it is difficult or impossible to achieve the required test values without gasketing. So we rely on the gasketing manufacturers, who test each of their products and list them as compliant with UL 1784 and appropriate for use on doors with smoke control requirements (S-labeled).

In addition to smoke control, IBC for several years has been requiring fire doors to be tested according to the UL10C positive pressure test that is more representative of an actual fire than the old negative or neutral pressure tests. Under UL 10C, a neutral pressure level is established at 40 inches above the floor, causing positive pressure forces against the door assembly above the neutral line. Because hot gases leak out in the positive pressure area, wood doors require an intumescent sealing system either built into the door, or applied to the frame. Once again, we rely on gasketing manufacturers to test their products as compliant with UL 10C.

Regarding the door bottom, there has been much confusion in the past about the requirement for a bottom seal. Under the UL 10C testing procedure, the sill of the door is under negative pressure because the neutral line is at 40 inches. Therefore we typically don’t specify door bottom seals for fire rated openings. Examples of exceptions are: 1) where there is a sound control requirement; 2) where there is a mechanically pressurized space such as a pressurized stairwell, a laboratory space, or a mall; or 3) where the authority having jurisdiction requires a door bottom in addition to the code requirement. Note that if a door bottom is used even if not required by code, it still needs to be rated accordingly to the rating of the door, just like any other item of hardware.

Now, one reason for the confusion over the door bottom is that the UL 1784 test calls for an “artificial door bottom” installed at the sill of the specimen door being tested. The reason UL does this is that the test is meant to evaluate gasketing at the door edges (head and jambs) and since there is no neutral pressure line in this test protocol like there is in UL 10 C, if the bottom were left open it would skew the test results on the gasketing. And in fact, when IBC came out with these requirements, they put out an interpretation clarifying that they did not require a door bottom to be installed in the assembly – it was only a requirement for the test apparatus.
George A. Everding AIA CSI CCS CCCA
Ingersoll Rand Security Technologies
St. Louis, MO
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1071
Registered: 03-2003


Posted on Friday, December 21, 2012 - 04:56 pm:   Edit PostDelete PostPrint Post

George: I think you nailed it.
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
George A. Everding, AIA, CSI, CCS, CCCA
Senior Member
Username: geverding

Post Number: 761
Registered: 11-2004


Posted on Tuesday, August 26, 2014 - 02:00 pm:   Edit PostDelete PostPrint Post

Former colleague at Allegion Lori Greene had a related post in her "I Dig Hardware" blog recently: http://idighardware.com/2014/08/gasketing-on-stair-doors/

Topics | Last Day | Last Week | Tree View | Search | Help/Instructions | Program Credits Administration