Can anyone give me a brief list of the pros and cons of extruded polystyrene and rigid mineral wool insulation for interior applications? Why would one be preferable of the other?
Ralph Liebing, RA, CSI, CDT
Senior Member
Username: rliebing

Post Number: 1277
Registered: 02-2003
Posted on Monday, December 05, 2011 - 11:10 am:   Edit PostDelete PostPrint Post

Check the following [and related links] for many types of insulation and explanations:

http://www.industrialinsulation.com/board_insulation.htm
Wayne Yancey
Senior Member
Username: wayne_yancey

Post Number: 501
Registered: 01-2008


Posted on Monday, December 05, 2011 - 11:12 am:   Edit PostDelete PostPrint Post

Extruded Polystyrene (XPS):
Pros: Typical R-value of 5/inch; moisture tolerant; low moisture absorption; low water vapor permeance (effective as a vapor retarder at about 1 inch or more thickness); can be adhered or mechanically attached.
Cons: Flamable (some jurisdictions may not allow in non-combustible walls); requires a 15 minute thermal barrier; does not conform to imperfections in substrate walls.

FYI, Mineral wool is considered semi-rigid, not rigid.

Semi-Rigid Mineral Wool:
Pros: Moisture tolerant; low moisture absorption but higher than polystyrent or spray foam; permeable to water vapor, non-flammable (unfaced FS/SD of 0/0); can be left exposed to view; available with Class 1(A) facing; conforms better to irregularities in substrates.
Cons: Requires mechanical attachment; Typical R-value of 4.2 per inch; facing not protected by gypsum board subject to damage.
Gerard Sanchis
Senior Member
Username: gerard_sanchis

Post Number: 59
Registered: 10-2009


Posted on Monday, December 05, 2011 - 11:43 am:   Edit PostDelete PostPrint Post

I won't compare the two types line by line, but the main difference is flammability and especially toxicity under fire conditions for plastic insulation.

Plastic insulation is also dimensionally unstable.
Anne Whitacre, FCSI CCS
Senior Member
Username: awhitacre

Post Number: 1218
Registered: 07-2002


Posted on Monday, December 05, 2011 - 04:30 pm:   Edit PostDelete PostPrint Post

despite the question, why are you thinking of EITHER of those insulations for interior work? typical in an interior condition would be fiberglass, either faced or unfaced.
Mineral wool is typically expensive and is used for flammability reasons (and typically at the exterior, but not always) and I can't think of a code agency that would allow EPS on the interior of a building in anyform unless fully encapsulated in a concrete floor. (I have used it once in a while where we needed to build up thickness but not weight for a podium -- and used the high density version).
J. Peter Jordan (Unregistered Guest)
Unregistered guest
Posted on Monday, December 05, 2011 - 04:26 pm:   Edit PostDelete PostPrint Post

There are a number of different types of "plastic insulation" products of which the extruded polystyrene is one. These are usually specified according to ASTM C 578. Molded polystyrene also fall under this spec. There are differences in terms of open/closed cell, R-values, and densities. Polyiso (another type of rigid plastic insulation) is specified under ASTM C 1289 and has several different types as well. Pay particular attention to applicable code requirements on "plastic insulation." This can get kinda hairy if you don't watch out.
ken hercenberg
Senior Member
Username: khercenberg

Post Number: 109
Registered: 12-2006
Posted on Tuesday, December 06, 2011 - 06:06 pm:   Edit PostDelete PostPrint Post

Plastic insulation: Toxic smoke potential
Mineral fiber, including glass fiber: Airborne irritant potential.

Considering my personality, I'll advocate for irritants.
Richard L Matteo, AIA, CSI, CCS
Senior Member
Username: rlmat

Post Number: 468
Registered: 10-2003
Posted on Tuesday, December 06, 2011 - 08:06 pm:   Edit PostDelete PostPrint Post

The irritant may irritate you, but it probably won't kill you. On the other hand, many people have died from smoke inhalation that contained fumes from burning plastic insulation.
Robin E. Snyder
Senior Member
Username: robin

Post Number: 381
Registered: 08-2004
Posted on Tuesday, December 06, 2011 - 10:45 pm:   Edit PostDelete PostPrint Post

Interesting answers. I am a bit confused because there seems to be several expanded polystyrene products that are marketed for interior walls.

So, when you are faced with interior furring, with a small cavity for insulation, (let's say less than 3 inches), what insulation do you recommend?
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 975
Registered: 03-2003


Posted on Tuesday, December 06, 2011 - 11:04 pm:   Edit PostDelete PostPrint Post

There is no prohibition in the building code to using foam plastic insulation on interior walls.

The only requirement beyond the maximum smoke developed and flame spread indeces is the requirement to provide a thermal barrier between the foam insulation and the interior of a building. The prescriptive requirement is applying a layer of 1/2-inch-thick gypsum board or a material that will survive 250 degrees for 15 minutes complying with the ASTM E 119 time-temperature curve.
Ron Geren, AIA, CSI, CCS, CCCA, SCIP
www.specsandcodes.com
Thomas E. Momeyer, AIA, CCS, LEED AP BD+C
Intermediate Member
Username: tmomeyer

Post Number: 4
Registered: 03-2007
Posted on Wednesday, December 07, 2011 - 12:01 am:   Edit PostDelete PostPrint Post

Robin,

You rec'd a lot of responses and said, "I am a bit confused..." It would help if you noted your application a bit more specific than interior use (comparing extruded polystyrene to rigid mineral wool). If you're talking about using rigid insulation on an exterior masonry or concrete wall, I've specified extruded polystyrene with Z furring in those applications for 1-6 story buildings and never mineral wool.

Is the application against an exterior wall? If so, what is the wall construction and proposed interior finish? Is this a high-rise building?
Thomas E. Momeyer, AIA, CCS, LEED AP BD+C
Lisa Goodwin Robbins, RA, CCS, LEED ap
Senior Member
Username: lgoodrob

Post Number: 157
Registered: 08-2004
Posted on Wednesday, December 07, 2011 - 08:54 am:   Edit PostDelete PostPrint Post

Robin,
I have a client who often renovates older buildings constructed with single wythe CMU walls. They like to put metal studs and extruded polystyrene insulation on the inside face of the wall, then cover it with GWB. The existing 8-12 inch thick wall is an air barrier (in theory); this doesn't make it a super high performing wall; but it seems to work well enough; it passes the Massachusetts Energy Code.
Is this what you are thinking about?
-
Lynn Javoroski FCSI CCS LEEDŽ AP SCIP Affiliate
Senior Member
Username: lynn_javoroski

Post Number: 1346
Registered: 07-2002


Posted on Wednesday, December 07, 2011 - 09:55 am:   Edit PostDelete PostPrint Post

Perhaps one of the foamed-in-place insulations would work?
Steven Bruneel, AIA, CSI-CDT, LEED-AP
Senior Member
Username: redseca2

Post Number: 307
Registered: 12-2006


Posted on Wednesday, December 07, 2011 - 01:22 pm:   Edit PostDelete PostPrint Post

If you need to achieve an R-value within a limited space you might want to look into some of the nanotechnology aerogel insulation products that are coming on line.

Look at Aspen Aerogel "Spaceloft" and Cabot's "Thermal Wrap" come in thin rolls usually less than 0.5-inch thick.
Anne Whitacre, FCSI CCS
Senior Member
Username: awhitacre

Post Number: 1220
Registered: 07-2002


Posted on Wednesday, December 07, 2011 - 02:15 pm:   Edit PostDelete PostPrint Post

Robin-
you're still not saying what you want the insulation for. there are a lot of small cavities that are just left as small cavities. are you insulating for sound, temperature differential; is there moisture; is there air blowing through there? each of them might suggest a completely different answer.
Robin E. Snyder
Senior Member
Username: robin

Post Number: 382
Registered: 08-2004
Posted on Thursday, December 08, 2011 - 12:32 pm:   Edit PostDelete PostPrint Post

I appreciate all the answers..my thought process switched mid-stream, that's why my questions sounded all over the place. The first few responses implied that extruded polystyrene is never used on the interior of a building for any purpose, but my confusion came because I know there are several commercial products that are intended for that very use. So, why would they marked products that are prohibited by code.
Ron, you cleared things up, so I think I understand now. Thanks,