We are beginning the process of reviewing the submittals we typically require to identify those that are unnecessary, in the hope of conserving Construction Phase time. I expect we will have different requirements applying to different project categories. If anyone has been through this process lately, I would appreciate any wisdom you can share. |
Nathan Woods, CCCA, LEED AP Senior Member Username: nwoods
Post Number: 214 Registered: 08-2005
| Posted on Tuesday, July 10, 2007 - 06:57 pm: | |
One effective technique is to classify non-critical submittal items as Informational verses Action submittals. For example, you might omit MSDS's from the required Action submittals and make them informational. As the architect, I don't review MSDS's, but I do want the contractor to have them. |
Ronald L. Geren, RA, CSI, CCS, CCCA, SCIP Senior Member Username: specman
Post Number: 493 Registered: 03-2003
| Posted on Tuesday, July 10, 2007 - 07:32 pm: | |
Nathan: If it's in the specification as a submittal, then you're requiring the contractor to give it to you. The difference between an "Informational" and an "Action" submittal is what the architect does after it is submitted to him/her. Informational submittals are given to the architect for his/her information only, and no response is necessary unless the submittal doesn't comply with requirements. On the other hand, action submittals require a response from the architect so that the contractor knows if the submittals are approved or not. T.A. Gilmore: I haven't been through that process, but each of my clients have different needs when it comes to submittals. I've asked them to identify what submittals they want and I edit the specs accordingly. You can create a submittal list for each section and ask that the PMs, designers and CAs to check off those that they want. Additionally, the checklist can identify those submittals that are the office "minimums" and the rest are considered optional. I think it will be difficult to create a system that will cover every possible project type, delivery method, and construction. |
Anne Whitacre, FCSI CCS Senior Member Username: awhitacre
Post Number: 587 Registered: 07-2002
| Posted on Tuesday, July 10, 2007 - 08:36 pm: | |
Keep in mind that there are a whole bunch of submittals that are required if you are going after a LEED certification; you might classify those as a whole different category. |
Doug Frank FCSI CCS Senior Member Username: doug_frank_ccs
Post Number: 193 Registered: 06-2002
| Posted on Wednesday, July 11, 2007 - 09:21 am: | |
We’ve been limiting submittals to be reviewed and processed by us for several years with little problem. We have identified stuff that we don’t care to see (like a sample of a piece of gyp bd for example) and do not request that particular submittal. We don’t really need to see product data for a bunch of stuff as well and exclude many of those from our required list as well. In fact, for a select few product types, we say that if you’re going to provide the exact product / manufacturer / model number / etc that we have spec’d,, don’t send us any submittals. Obviously that’s not the case for curtainwall and other complex Systems but it does work for toilet accessories and such. Be very careful about how you limit submittals though. It’s imperative that the Contractor have all the appropriate shop drawings, product data, etc. from his subs even if you don’t want to see them. For this we tell the Contractor that he has to maintain a copy of all submittals at the job site and we’ll look at them periodically before processing pay apps. |
T.A. Gilmore, AIA, CCS, CCCA, LEED AP Senior Member Username: tgilmore
Post Number: 7 Registered: 04-2007
| Posted on Wednesday, July 11, 2007 - 12:32 pm: | |
Thanks! We already classify submittals in 5 categories including pre-procurement (elevators usually), action, LEED, information, and closeout. I coach our CA architects how to deal with information submittals, and that has helped. There still needs to be some education for the Owners and Contractor about our response to info submittals. We separate action and information submittals based on the PRM. Ron, are you suggesting that we might reassign shop drawings for example from action to information submittal category? |
Ronald L. Geren, RA, CSI, CCS, CCCA, SCIP Senior Member Username: specman
Post Number: 494 Registered: 03-2003
| Posted on Wednesday, July 11, 2007 - 12:55 pm: | |
T.A. Gilmore: I'm not suggesting it, but shop drawings can be submitted in whatever manner you want them to be submitted. If you don't want to mark up shop drawings and return them to the contractor, then they could be considered "informational," provided Section 01 33 00, Submittal Procedures, states that shop drawings are informational submittals. However, if you do consider shop drawings as informational, as a courtesy to the contractor, I would let them know through some direct communication (preconstruction meeting, letter, etc.) in addition to the specifications. Tradition is hard to change, even if it's clearly stated in the specs; and, you don't want the contractor sitting around for a response that will never come. |
George A. Everding, AIA, CSI, CCS, CCCA Senior Member Username: geverding
Post Number: 329 Registered: 11-2004
| Posted on Wednesday, July 11, 2007 - 01:18 pm: | |
Twice recently I've been through the process of evaluating submittals required. I'd be happy to share the executive summary from one committee that looked at submittals, along with a list of excellent references on the subject. Email geverding@cannondesign and I'll send by return email. The informational/action break can be very valuable in reducing a/e time and effort (not to mention liability). It is interesting to note that the new Section Format addresses a distinction between information and action submittals. For MasterSpec users, the evaluations for 01 3300 is a good background. |
George A. Everding, AIA, CSI, CCS, CCCA Senior Member Username: geverding
Post Number: 330 Registered: 11-2004
| Posted on Wednesday, July 11, 2007 - 01:59 pm: | |
....er....cannondesign.com as pointed out to me in a just received email. |
David J. Wyatt, CSI, CCS, CCCA (Unregistered Guest) Unregistered guest
| Posted on Thursday, July 12, 2007 - 04:05 pm: | |
Has anyone, as a means of reducing the number of submittals, requested a "Letter of Conformance"? I have a client who wants to implement this process and has done so in the past with some good results. Obviously some submittals are necessary (steel shop drawings, fire performance data for AHJs, etc.), so the LOC cannot completely supplant the submittal review process. |
Nathan Woods, CCCA, LEED AP Senior Member Username: nwoods
Post Number: 215 Registered: 08-2005
| Posted on Thursday, July 12, 2007 - 08:30 pm: | |
I've only allowed "Letter of Conformance" type submittal on phased projects, where Phase 2 incorporates the same materials, and more importantly, the same sub-contractors as the origional phase. |
Phil Kabza Senior Member Username: phil_kabza
Post Number: 270 Registered: 12-2002
| Posted on Thursday, July 12, 2007 - 09:39 pm: | |
I've occasionally specified or allowed LOC use for items that are not HSW/life safety issues or building envelope issues. |
Jerome J. Lazar, RA, CCS, CSI, SCIP Senior Member Username: lazarcitec
Post Number: 394 Registered: 05-2003
| Posted on Friday, July 13, 2007 - 12:39 am: | |
Marriott International references Letters of Conformance in their Guide Specs. The Guide specs include a form that is titled "Letter of Conformance" that must be completed by GC and submitted, the following is an excerpt: "This Letter of Conformance is provided as a Submittal for Information in accordance with Section 01330 (01 33 00) - Submittals and Substitutions. The undersigned hereby declares that the Product identified above by manufacturer's name and model number is (one of) the product(s) specified and is suitable for the intended use as defined within the Contract Documents and will be provided and placed in operational condition in accordance with the manufacturer's published instructions and the Contract Documents." Marriott defines LOC's as: "Short-form informational submittals which are to be used instead of shop drawings, product data and samples. They are also to be used to supplement shop drawings, product data and samples." |
John Bunzick, CCS, CCCA Senior Member Username: bunzick
Post Number: 753 Registered: 03-2002
| Posted on Friday, July 13, 2007 - 12:14 pm: | |
Also know as a product or material certificate, included in the text of many Masterspec sections. |
T.A. Gilmore, AIA, CCS, CCCA, LEED AP Senior Member Username: tgilmore
Post Number: 8 Registered: 04-2007
| Posted on Friday, July 13, 2007 - 12:18 pm: | |
This has been helpful. What I am really looking for are some principles to guide me in the judicious pruning back of our submittal requirements that, being a conservative specifier, I tend to choose just because they might in some cases reduce our risk, or help avoid having the Contractor do something stupid. Where is that fine line between due diligence (the standard of care) and too much monkey business? |
Jerome J. Lazar, RA, CCS, CSI, SCIP Senior Member Username: lazarcitec
Post Number: 395 Registered: 05-2003
| Posted on Friday, July 13, 2007 - 12:41 pm: | |
T.A. Take a look at Andrew Civitello's book - "Contractor's Guide to Change Orders" (maybe you can borrow a copy), he has a chapter on "Approval Submissions" addressing it from the Contractor's viewpoint - worth the read. I'll check my library, I seem to recall another book out there that may shed some light on your concerns - perhaps Ralph or Tom H (if they are lurking out there) can chime in with some sage advice. |
Ralph Liebing, RA, CSI Senior Member Username: rliebing
Post Number: 656 Registered: 02-2003
| Posted on Friday, July 13, 2007 - 01:14 pm: | |
Lurking???????????? Jerome, I'm getting qualms about you as my PR guy! I am willing to share our recent revision of our submittals policy, if any one is interested. It started with the concept of "Zero Submittals". Don't gag! We were suffering from submittal text in our masters that our Project Leads just let slide over, project to project, producing needless submitals. So we went with the MasterSpec submittal categories, and stripped all residual text from our masters. NOW, the Leads must think IF they really need/want a submittal, and WHAT specifically they want to see. End of synopsis-- interested? e-mail me |
Jerome J. Lazar, RA, CCS, CSI, SCIP Senior Member Username: lazarcitec
Post Number: 396 Registered: 05-2003
| Posted on Friday, July 13, 2007 - 01:32 pm: | |
Qualms!!!!! I don't have time to do PR for my own firm (that's probably a good thing) so you need not worry - I just know that you are a wealth of information, and if you don't know it, or don't know how to get it, well, TA is really in trouble. |
Don Harris CSI, CCS, CCCA, AIA Senior Member Username: don_harris
Post Number: 145 Registered: 03-2003
| Posted on Friday, July 13, 2007 - 03:11 pm: | |
Civitello's book is excellent. I read it because of a recommendation in a previous thread here. One word of caution, reading it from the point of view of an architect or specifier, it sort of reads like the Texas Chainsaw Massacre. It is very graphic and very stomach churning. Highly enlightening though. |
Jerome J. Lazar, RA, CCS, CSI, SCIP Senior Member Username: lazarcitec
Post Number: 398 Registered: 05-2003
| Posted on Friday, July 13, 2007 - 03:43 pm: | |
Don, back on Feb 23, 2007 I started a thread called 'OneBook' and Andrew's book was my one book, though later others were mentioned. It is a scary book to read, but how often as a specwriter can you get a glimpse of the mind of a Contractor, esp. when it comes to Change Orders. I own both the first and second editions, and only wish I had time to fully read them fully, but I have read, flagged, and have used portions of the book in my work. |
Anonymous
| Posted on Friday, July 13, 2007 - 03:45 pm: | |
Civitello's book is certainly an interesting read. I needed to take a shower when I was done though. It just feels so immorally dirty! |
Jerome J. Lazar, RA, CCS, CSI, SCIP Senior Member Username: lazarcitec
Post Number: 399 Registered: 05-2003
| Posted on Friday, July 13, 2007 - 03:51 pm: | |
Don, I think what we need here is for Ralph and John to collaborate on a book entitled "Everything You Wanted To Know About Shop Drawings and Submittals, But Were Afraid (or too Stupid) to Ask". It should be short and to the point, 100 pages or less, even spiral bound, and of course organized according to CSI Masterformat 1995 (I hate 2004)...what do you think, maybe if we all emailed Ralph and John it would convince them that we need this....especially on Friday the 13th. |
Susan McClendon Senior Member Username: susan_mcclendon
Post Number: 69 Registered: 01-2005
| Posted on Thursday, October 04, 2007 - 11:06 am: | |
Doug Frank said "It’s imperative that the Contractor have all the appropriate shop drawings, product data, etc. from his subs even if you don’t want to see them." In this situation, do people call for shop drawings to be submitted directly to the contractor? or what? |
Ronald L. Geren, AIA, CSI, CCS, CCCA, SCIP Senior Member Username: specman
Post Number: 538 Registered: 03-2003
| Posted on Thursday, October 04, 2007 - 11:16 am: | |
I only specify what the architect wants to see. If the contractor wants more than that, they'll need to add that to their contractor-subcontractor agreements. I don't want to get into the middle of the contractor's business beyond what the architect is required to do. |
Richard L Matteo, AIA, CSI, CCS Senior Member Username: rlmat
Post Number: 243 Registered: 10-2003
| Posted on Thursday, October 04, 2007 - 11:39 am: | |
Ralph, I have a similar issue im my firm. We tend to ask for many more submittals than are necessary, but it's difficult at best to weed out the unnecessary ones. And you're right - I don't get any help from my PA's or Project Leads. my e-mail is rmatteo@tbparchitecture.com |
Tom Heineman RA, FCSI, SCIP Senior Member Username: tom_heineman
Post Number: 90 Registered: 06-2002
| Posted on Thursday, October 04, 2007 - 01:11 pm: | |
Many of us have had PART 3 requirements such as "have a copy of approved submittals at the worksite" and "install following spproved submittals". Now, with the layering of submittals into informational, LEED, and action, we must take another look at those two requirements. Must LEED submittals be kept at the trailer? Must installation follow what is in the informational submittals? Check your PART 3 language now. Some of us have introduced a time dimension. I require an Early Submittal for some things, and specify that no further submittals be made until the Early Submittal has been approved. Most frequently this is used for crucial Special Warranty text - for which I want to see the letter or form - specific to the job - that the contractor is going to submit at closeout. I usually do not list specific Closeout Subnmittals in the Submittals article because these are much the same for all sections and can be pretty well covered in 01 78 00. |
Anonymous
| Posted on Thursday, October 04, 2007 - 11:57 am: | |
Definitely don't need samples for initial selection when the color/texture/pattern whatever is indicated. Another one I may often delete is preinstallation conference (ONLY on sections that do not involve much coordination, on simpler projects of course). One way to give the PA a quick read on what is left is to print a MasterWorks submittals report, and if the CA is assigned to the project before it goes to bid then give them a copy first. They'll be happy to scratch off a few before you give it to the PA for final review. It would be great to get an Owner who is truly involved to also take a look, but I don't see that level of interest from them very often, even though our firm does a wide range of project types. We almost have to chain them to a desk to even get them to even tell us $ amounts for liquidated damages and insurance limits. They seem to think we would just intuitively know all their desires, us being the specifiers and design professionals of course. |
|