Jerome J. Lazar, CCS, CDT, CSI, SCIP
Senior Member
Username: lazarcitec

Post Number: 2065
Registered: 05-2003
Posted on Wednesday, October 30, 2019 - 04:56 pm:   Edit PostDelete PostPrint Post

WHERE IN A TYPICAL CONCRETE UNIT MASONRY SPEC SECTION IS THE FIRE RATING SPECIFIED?
Brian Payne
Senior Member
Username: brian_payne

Post Number: 200
Registered: 01-2014
Posted on Wednesday, October 30, 2019 - 05:00 pm:   Edit PostDelete PostPrint Post

It isn't for me. The fire rating is indicated in the drawings. Section 721/722 of the code gives prescriptive/calculated thicknesses required to meet hourly ratings.
Jerome J. Lazar, CCS, CDT, CSI, SCIP
Senior Member
Username: lazarcitec

Post Number: 2066
Registered: 05-2003
Posted on Wednesday, October 30, 2019 - 05:02 pm:   Edit PostDelete PostPrint Post

Brian, the Architect is insisting I add the fire rating to the spec section, specifically for two hour rating.
Brian Payne
Senior Member
Username: brian_payne

Post Number: 201
Registered: 01-2014
Posted on Wednesday, October 30, 2019 - 05:05 pm:   Edit PostDelete PostPrint Post

Typically, the only impact the rating has for a 2HR block wall is on the firestopping at the penetrations and any openings. Otherwise, the cmu doesn't change for a nonrated, 1 HR, or 2HR wall. 3 Hr requirements can sometimes exceed the face thickness of standard cmu block.
Brian Payne
Senior Member
Username: brian_payne

Post Number: 202
Registered: 01-2014
Posted on Wednesday, October 30, 2019 - 05:10 pm:   Edit PostDelete PostPrint Post

Fire Resistive Rating: As indicated on Drawings.

Done! :-)
George A. Everding, FCSI, CCS, CCCA, AIA
Senior Member
Username: geverding

Post Number: 904
Registered: 11-2004


Posted on Wednesday, October 30, 2019 - 05:18 pm:   Edit PostDelete PostPrint Post

Jerry-

See NCMA Tek notes, particularly this one: https://ncma.org/resource/fire-resistance-ratings-of-concrete-masonry-assemblies/ This tech note refers to IBC 722 as Brian mentions.

There are other Tek Notes that might be relevant to your question - you can search the NCMA Tek Notes for Fire Rating. For Example 05-08B is a good reference for how to address fire ratings on Drawing Details.
Jerome J. Lazar, CCS, CDT, CSI, SCIP
Senior Member
Username: lazarcitec

Post Number: 2067
Registered: 05-2003
Posted on Wednesday, October 30, 2019 - 05:21 pm:   Edit PostDelete PostPrint Post

Client is stubborn, they are insisting I include in spec section, but where, how?
Marc Chavez
Senior Member
Username: mchavez

Post Number: 533
Registered: 07-2002
Posted on Wednesday, October 30, 2019 - 05:22 pm:   Edit PostDelete PostPrint Post

Back to Jerome's initial question....IF you need to place it in the specs. (I also try to have this on the drawings as code officials are looking for it there) Make a performance requirement article in part 2 and place the appropriate language there... mentioning the IBC chapter and verse. then back in part one in related requirements list the fire stopping section
Paul Sweet (Unregistered Guest)
Unregistered guest
Posted on Wednesday, October 30, 2019 - 05:10 pm:   Edit PostDelete PostPrint Post

The drawings should show where the different ratings (or unrated block) go.
Part 2 of the specs should say what type of block is required for different ratings.
Monsterspec is written around UL U906 and a lot of A/E's blindly require it, even though it requires a stamp on the block that increases the cost of the block. I always use the equivalent thickness method of IBC 721 722. You can get a 2 hour rating from regular block with solite or similar aggregate, and 3 or 4 hours with 75% solid block.
Mark Gilligan SE,
Senior Member
Username: mark_gilligan

Post Number: 918
Registered: 10-2007
Posted on Thursday, October 31, 2019 - 03:49 pm:   Edit PostDelete PostPrint Post

As stated the code provides prescriptive fire rating for a certain type of block construction. It does not need to be shown on the drawings.

If you listed the fire rating of the block ask yourself what do you expect the contractor to do to show that he has complied?

I suspect that this is really in response to UL's program where they perform a fire test on a specific manufacturers block thus allowing the manufacturer to apply a mark/label to their block. This is just your generic concrete block.

There is no difference between the concrete block with the UL rating and the concrete block assembly listed in the building code. UL then uses this process to pressure concrete block manufacturers to pay UL to perform the test and allow them to place the mark on their block.

I repeat there is no technical justification for requiring UL certified concrete block. It only increases the cost to the Owner.

When UL performs fire tests of fire caulking in a masonry wall they then list as part of the assembly concrete block units that have their certification

Since the fire caulking UL test assumes an assembly with UL certified block the caulking cannot be used on block walls that do not have the certification. This means that if the block in an existing building was manufactured before the UL program you cannot place a new hole in the existing wall.

I suggest that UL is using their market power to create a monopoly for themselves.
ken hercenberg
Senior Member
Username: khercenberg

Post Number: 1252
Registered: 12-2006


Posted on Thursday, October 31, 2019 - 04:19 pm:   Edit PostDelete PostPrint Post

Hi Jerry.
So as Mark noted, in order for the GC to document compliance they will need to buy UL-certified CMU which will increase the cost to the client.

Perhaps the Architect would like to confirm that is the intent, to add unnecessary cost to the client. I'd ask for that in writing for sure.
Marc Chavez
Senior Member
Username: mchavez

Post Number: 534
Registered: 07-2002
Posted on Thursday, October 31, 2019 - 04:39 pm:   Edit PostDelete PostPrint Post

IMHO, No. they do not need to buy UL certified block. they need only to show the code official the product they are building with (sim to what they do with mortar and bricks) and a clip from the IBC if needed to reinforce the fact that it is allowed. No UL certification needed BECAUSE they have the building code....do we ask for UL certification for 2 hour concrete walls? no. we just measure the thickness and perhaps if forced, a mix design. Also. I have done this many times and had no problem, in the spec, on a table in the dwgs, on assys in the dwgs, never an issue.
Brian E. Trimble, CDT
Senior Member
Username: brian_e_trimble_cdt

Post Number: 115
Registered: 08-2005


Posted on Thursday, October 31, 2019 - 04:47 pm:   Edit PostDelete PostPrint Post

Agree with all the posters above. You can put the requirements for the necessary type of block (aggregate type, void percentage) in Part II of the masonry section. You can ask for certificates from the block manufacturer to show they meet what was specified. As previously mentioned - no need to get UL ratings when equivalent thickness is a code-approved procedure.
John Bunzick, CCS, CCCA, LEED AP
Senior Member
Username: bunzick

Post Number: 1795
Registered: 03-2002
Posted on Thursday, October 31, 2019 - 05:43 pm:   Edit PostDelete PostPrint Post

Also, if a partition is NOT shown to be rated, but is constructed with UL-labeled CMU, that doesn't mean it meets the code as a rated partition. Fire stopping, treatment of embedded items, etc. come into play.
Ronald L. Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Senior Member
Username: specman

Post Number: 1570
Registered: 03-2003


Posted on Thursday, October 31, 2019 - 05:48 pm:   Edit PostDelete PostPrint Post

I just specify the equivalent thickness based on the worse case aggregate condition (Calcareous or siliceous gravel). Any of the other lighter aggregates (or combination thereof) will only increase the fire resistance for the specified equivalent thickness.
Ron Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP

Topics | Last Day | Last Week | Tree View | Search | Help/Instructions | Program Credits Administration