I am intrigued by this product. Has anyone used T-Studs thermally broken wood studs on a project? https://www.tstud.com/ This product seems to be more of a residential product but here in the Pacific Northwest we use a lot of wood for Low and Midrise projects. We do that because of cost (wood is cheaper than steel) and thermal performance. David G. Axt, CCS, CSI, SCIP Specifications Consultant Axt Consulting LLC |
anon (Unregistered Guest) Unregistered guest
| Posted on Thursday, August 22, 2019 - 01:11 pm: | |
Where is NFPA 285 test for anything greater than a story in height? |
An (Unregistered Guest) Unregistered guest
| Posted on Thursday, August 22, 2019 - 05:48 pm: | |
I'm assuming this would qualify as Type V construction and wouldn't need NFPA 285 testing (reference 2015 IBC 2603.5 and note that Type V construction need not comply with 2603.5.5 "Vertical and lateral fire propagation"). |
anon (Unregistered Guest) Unregistered guest
| Posted on Thursday, August 22, 2019 - 06:12 pm: | |
Yes, that exception might apply to some low and midrise projects, but confident there are many that would not make that classification, in which case this product would be verboten unless tested/passed in accordance with NFPA 285, as I understand the IBC requirements for use of foam plastic in exterior assemblies. |
Paul Sweet (Unregistered Guest)
Unregistered guest
| Posted on Friday, August 23, 2019 - 12:31 pm: | |
I don't know of any reference to NFPA 285 in the International Residential Code. The R value of 20 for 2 1/2" of foam insulation looks high to me. I'd be nervous about the nail holding power of only 1/2" of wood on each side of the foam in a 2 x 4. |
Dewayne Dean Senior Member Username: ddean
Post Number: 201 Registered: 02-2016
| Posted on Friday, August 23, 2019 - 02:22 pm: | |
What Paul said |
Anne Whitacre, FCSI CCS Senior Member Username: awhitacre
Post Number: 1462 Registered: 07-2002
| Posted on Friday, August 23, 2019 - 03:21 pm: | |
How much heat transfer actually occurs through wood studs? we use thermally broken metal parts regularly now, but I didn't realize this was much of an issue with dry wood. |
John Bunzick, CCS, CCCA, LEED AP Senior Member Username: bunzick
Post Number: 1791 Registered: 03-2002
| Posted on Friday, August 23, 2019 - 03:28 pm: | |
Does the residential code require continuous insulation the way the "commercial" code does? This would seem to meet that requirement, although I, too, am squeamish about the structural capability. What's the chance of shear failure through this foam "web." |
David G. Axt, CCS, CSI ,SCIP Senior Member Username: david_axt
Post Number: 1822 Registered: 03-2002
| Posted on Friday, August 23, 2019 - 06:59 pm: | |
Residential code does not require continuous insulation....yet. The studs are stronger than solid wood framing. David G. Axt, CCS, CSI, SCIP Specifications Consultant Axt Consulting LLC |
anon (Unregistered Guest) Unregistered guest
| Posted on Friday, August 23, 2019 - 01:31 pm: | |
Isn't the IRC for one and two family dwellings? I don't think lowrise and midrise projects mentioned by OP would be governed by the IRC. |
Brett Scarfino (Unregistered Guest)
Unregistered guest
| Posted on Monday, August 26, 2019 - 09:42 am: | |
Anne - To your point, here are some generic/relative thermal conductivity values. I would consider wood to be a very poor conductor while being a marginal insulator...if that makes any sense. 0.08 softwood 0.07 urethane thermal break 0.015 XPS insulation 0.6 glass 35 steel 10 stainless steel 92 alum. alloys |
David G. Axt, CCS, CSI ,SCIP Senior Member Username: david_axt
Post Number: 1823 Registered: 03-2002
| Posted on Monday, August 26, 2019 - 12:47 pm: | |
According to this website: http://www.coloradoenergy.org/procorner/stuff/r-values.htm 2x4's R-value = 4.38 (U-Value = 0.228) 2x6's R-value = 6.88 (U-Value = 0.145) T-Stud 2x6 R-value = 20 (U-Value = 0.05) David G. Axt, CCS, CSI, SCIP Specifications Consultant Axt Consulting LLC |
Paul Sweet (Unregistered Guest)
Unregistered guest
| Posted on Monday, August 26, 2019 - 12:45 pm: | |
Wood studs have an R-value around 1.4 per inch, so a 2x4 would be R-4.9 and a 2x6 would be about 7.7. Using a more realistic R=5.6 for the foam, a 2x4 T Stud would be R15.4 and a 2x6 would be R18.2. Studs comprise a little over 10% of the wall area, so the overall difference isn't as significant as the difference in values for just the studs. |
Greta Eckhardt Senior Member Username: gretaeckhardt
Post Number: 106 Registered: 08-2013
| Posted on Monday, August 26, 2019 - 03:36 pm: | |
I am replacing my post from an hour or so ago, after realizing that the T-studs are only available as 2-1/2" x 5-1/2" studs, so the calculations had to be revised. Just as an example, using the R-values and U-values from Paul Sweet's post, I calculate the following area-weighted R-values: 2x6 nominal solid wood studs, 16" o.c. with R-20 batts between studs: R-17.21 2-1/2" x 5-1/2" T-studs, 16" o.c. with R-20 batts between studs: R-19.70 So there is a significant difference in overall thermal performance of the wall using the T-studs. |
Marc Chavez Senior Member Username: mchavez
Post Number: 516 Registered: 07-2002
| Posted on Monday, August 26, 2019 - 04:16 pm: | |
so for all the engineering and glue and foam I get a net increase of 2? how about we place 1 inch of plastic insulation continuously on the outside and get 5+ or even 1/2 inch and get 2.5 + no fancy studs needed..(yes I'd have to use clips)..too much fiddling around for too little benefit IMHO |
Guest (Unregistered Guest) Unregistered guest
| Posted on Monday, August 26, 2019 - 04:24 pm: | |
Mr. Chavez's view may change once the thermally-broken wood stud manufacturer pays avitru to include them in masterspec. |
Marc Chavez Senior Member Username: mchavez
Post Number: 517 Registered: 07-2002
| Posted on Monday, August 26, 2019 - 04:30 pm: | |
oh so cynical.....the manufacturer can ask all they want but ....not every product has an existing place in our TOC (and we don't just run out and write new sections for fun). Not every product makes it into MasterSpec regardless of money... but you can believe whatever you want. |
David G. Axt, CCS, CSI ,SCIP Senior Member Username: david_axt
Post Number: 1827 Registered: 03-2002
| Posted on Monday, August 26, 2019 - 05:47 pm: | |
I would be curious to hear what a structural engineer has to say about this product. T-Studs' video shows walls using only single top plates, 24 inch spacing and less wood to frame a window. I know from personal experience that good stable and straight 2x material is getting harder to find. That is why we are seeing more and more engineered wood on projects starting with plywood back in the forties and now I-joists, LVL, PSL, glulam, and most recently CLT. David G. Axt, CCS, CSI, SCIP Specifications Consultant Axt Consulting LLC |
Steven Bruneel, AIA, CSI-CDT, LEED-AP, EDAC Senior Member Username: redseca2
Post Number: 670 Registered: 12-2006
| Posted on Monday, August 26, 2019 - 06:09 pm: | |
I would expect a structural engineer would insist on "real" studs for king studs, perhaps at corners or anywhere where they want an additional tie down hardware, not to mention at sills, headers and top plates. So you are not even talking about all of the framing. |
J. Peter Jordan Senior Member Username: jpjordan
Post Number: 1104 Registered: 05-2004
| Posted on Tuesday, August 27, 2019 - 10:19 am: | |
Looking at their website, I would think that one of these is stronger that a conventional 2 b 6 stud. It is essentially a truss (really isn't thermally broken) with what appears to be 2 x material held together with wood dowels. More "stuff" at the extreme fibers to resist bending and, I believe a wwider member. I would be interested in looking at this to resist lateral wind load. J. Peter Jordan, FCSI, AIA, CCS, LEED AP, SCIP
|