This is a code requirement and it is not new. Yet designers have been directing me to use much smaller roof hatches for years.

Are others seeing a lot of roof hatches in designs that do not meet the code, or am I reading this wrong somehow?

[IBC][CBC] 1011.12.2 - Roof Access (Exception for Without an Occupied Roof): Roof hatch or trap door not less than 16 sq. ft. (1.5 sq. m) in area and having a minimum dimension of 2 feet (610 mm).

Confirmed below with IBC 2015, 2018; CBC 2016, 2019. For IBC 2012 the reference is 1009.16.1 but the information is the same.

I am starting to use Activar: RHDG-5WT, Roof Hatch, Diamond Series 48 inch by 48 inch as a placeholder with a question for the designer until they tell me something different.
Rosa Cheney
Member
Username: rdcaia

Post Number: 3
Registered: 07-2018
Posted on Friday, August 23, 2019 - 05:26 pm:   Edit PostDelete PostPrint Post

Chris, Maybe half of my Architect clients use the 16 sq. ft. size hatch. The others do once I point out the code reference.

I have heard (but don't recall where) that the size is to allow firemen with all their gear to get up through the hatch.

We use a 48x48 square for ladder access, and a rectangle for alternating tread stairs.
Paul Sweet (Unregistered Guest)
Unregistered guest
Posted on Saturday, August 24, 2019 - 01:25 pm:   Edit PostDelete PostPrint Post

This only applies to buildings 4 stories or higher. You can still use a smaller (30" x 36") hatch on lower roofs.
Brian Payne
Senior Member
Username: brian_payne

Post Number: 190
Registered: 01-2014
Posted on Saturday, August 24, 2019 - 02:15 pm:   Edit PostDelete PostPrint Post

And since high-rises require a stair to the roof (with exceptions) the larger roof hatch would only apply to buildings 4-7 stories without stair access I believe.
Chris Grimm, CSI, CCS, SCIP
Senior Member
Username: chris_grimm_ccs_scip

Post Number: 497
Registered: 02-2014
Posted on Sunday, August 25, 2019 - 10:19 am:   Edit PostDelete PostPrint Post

This is a 3-story building and the architect told me to follow that particular code reference. Any tips on how I can show them about it being four+ stories? I did not see that (yet ).
Ronald L. Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Senior Member
Username: specman

Post Number: 1563
Registered: 03-2003


Posted on Monday, August 26, 2019 - 11:44 am:   Edit PostDelete PostPrint Post

This requirement applies only if a roof hatch is used in lieu of a stair to the roof for buildings with four or more stories. A typical roof access hatch from a mechanical room or any other space is not restricted by this minimum area requirement.
Ron Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Guest (Unregistered Guest)
Unregistered guest
Posted on Monday, August 26, 2019 - 11:51 am:   Edit PostDelete PostPrint Post

nevermind, Ron Geren took care of it.
Guest (Unregistered Guest)
Unregistered guest
Posted on Monday, August 26, 2019 - 11:50 am:   Edit PostDelete PostPrint Post

First, understand that the requirement is for a hatch where there is stairway to the roof (1011.12.2 "Where a stairway is provided...") so if you don't have a stairway, you don't need the 16 sq. ft. hatch. I've seen this come up before, usually by someone who hasn't taken the time to read and understand the code. The reality is, if you have a stair to the roof, you usually get a much larger hatch than 16 sq. ft. (30"-36" x 96" is a common size for service stair access), or you get a door.

The code requires a stairway to the roof for buildings 4 or more stories above grade plane unless your roof is steeper than 4:12 (1011.12) and the roof is occupied (refer to language of exception in 1011.12). If you don't have an occupied roof, you don't need a stair*, and you don't need a 16 sq. ft. hatch. If you don't need a stair because your roof is unoccupied, most will simply include a permanent ladder, as allowed per the exception, and an appropriately sized roof hatch.

*There is another requirement for stairs to the roof if it is to access elevator equipment (see 1011.12.1).
Guest (Unregistered Guest)
Unregistered guest
Posted on Monday, August 26, 2019 - 12:51 pm:   Edit PostDelete PostPrint Post

ha ha, I didn't think my last two comments would get posted. The second was supposed to be the first, and was still a work in progress. It was accidentally submitted before it was finished. I then saw Ron's comment and realized it addressed it better than my post would have. The first was supposed to be the second simply indicating to Colin that he didn't need to bother posting the first. Oh well. Next time I'll try to be more clear, concise, complete, and correct.
David G. Axt, CCS, CSI ,SCIP
Senior Member
Username: david_axt

Post Number: 1824
Registered: 03-2002


Posted on Monday, August 26, 2019 - 12:53 pm:   Edit PostDelete PostPrint Post

I believe the reason for the large roof access hatch is to allow a firefighter in full gear with oxygen tank on their back to gain access to the roof.
David G. Axt, CCS, CSI, SCIP
Specifications Consultant
Axt Consulting LLC
RH (Hank) Sweers II RA CSI CCS
Senior Member
Username: rhsweers2

Post Number: 20
Registered: 08-2005
Posted on Monday, August 26, 2019 - 12:58 pm:   Edit PostDelete PostPrint Post

IBC Paragraph 1011.12 "Stairway to Roof" starts off with "In buildings four or more stories above grade plane . . . " so anything after that is moot with 3 stories or less. The code reference requiring a 16 SF access hatch is in a sub-paragraph of that (1011.12.2's "exception") permitting a hatch in lieu of a penthouse for access to an "unoccupied" roof. Can't hurt to oversize it though - I always spec a guardrail around the opening which isn't clearly required (except possibly by OSHA), but I'd rather have someone else not install it than to not have it specified.
Chris Grimm, CSI, CCS, SCIP
Senior Member
Username: chris_grimm_ccs_scip

Post Number: 500
Registered: 02-2014
Posted on Tuesday, August 27, 2019 - 01:10 pm:   Edit PostDelete PostPrint Post

Thanks everyone! My client really appreciated being corrected on this.

I THOUGHT something didn't seem quite right or many of my other clients would be violation.

To help make it easier for them (and me) in the future I have reflected this in my master:

[[IBC][CBC][ 1011.12.2] - Roof Access (For buildings having for four or more stories without an occupied roof): Provide roof hatch or trap door not less than 16 sq. ft. (1.5 sq. m) in area and having a minimum dimension of 2 feet (610 mm).]
Loretta Sheridan, CSI, CDT, MEng (Unregistered Guest)
Unregistered guest
Posted on Thursday, March 12, 2020 - 07:35 am:   Edit PostDelete PostPrint Post

This is really helpful!

I sometimes forget to go BACK to the parent paragraph when you get so far down in the subparagraphs.

The EXCEPTION modifies 1011.12.2 which modifies 1011.12:

1011.12 Stairway to roof. In buildings four or more stories above grade plane, one stairway shall extend to the roof surface....
1011.12.2 Roof access. Where a stairway is provided to a roof, access to the roof shall be provided through a penthouse...
EXCEPTION: In buildings without an occupied roof, access to the roof shall be permitted to be a roof hatch or trap door not less than 16 square feet in area and having a minimum dimension of 2 feet.
Chad Hanley (Unregistered Guest)
Unregistered guest
Posted on Tuesday, September 01, 2020 - 11:39 am:   Edit PostDelete PostPrint Post

Apologies on digging up an old thread, but what about the roof of the penthouse? Scenario: I have a building 4 or more stories, with a stairway to the main roof and access to that roof through a penthouse. Access to the penthouse roof is an internal ladder with a roof hatch (unoccupied roof). Based on the exception, wouldn't the roof hatch for the penthouse roof need to meet the 16 sf requirement? IBC doesn't really make a distinction between multiple roof levels.
Ronald L. Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Senior Member
Username: specman

Post Number: 1585
Registered: 03-2003


Posted on Tuesday, September 01, 2020 - 12:18 pm:   Edit PostDelete PostPrint Post

There is no requirement to provide access to the penthouse roof.
Ron Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Michael Chusid, RA FCSI CCS
Senior Member
Username: michael_chusid

Post Number: 552
Registered: 10-2003


Posted on Tuesday, September 01, 2020 - 03:39 pm:   Edit PostDelete PostPrint Post

Ron: Does the area of the penthouse make a difference in your statement, I have seen some very big "penthouses".

Chad: why not ladder on exterior of penthouse? You would have one less penetration through roof and probably reduce cost.
Michael Chusid, RA FCSI CCS 1-818-219-4937
www.chusid.com www.buildingproduct.guru
Marc Chavez
Senior Member
Username: mchavez

Post Number: 603
Registered: 07-2002
Posted on Tuesday, September 01, 2020 - 03:58 pm:   Edit PostDelete PostPrint Post

well more than 1/3 of the upper floor makes it a story! so area is important. (shaft wall terminations for example)
Ronald L. Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Senior Member
Username: specman

Post Number: 1586
Registered: 03-2003


Posted on Tuesday, September 01, 2020 - 04:28 pm:   Edit PostDelete PostPrint Post

As Marc states, a penthouse that exceeds 1/3 the roof area is no longer a penthouse and is now a story, and all the requirements for means of egress would apply (two exits, exit separation, travel distance, etc.).

The purpose of the roof access is to allow the fire department to access the inside of the building from the roof. If a roof has a penthouse, it would not make sense for the fire department to access the building through the penthouse roof (in many cases, one would have to exit the penthouse to get to a stairway or hatch making a penthouse roof access even more nonsensical).

Further, once on the roof, firefighters can either access the penthouse from the roof (if the fire is there) or into the building through the hatch or stairway. Thus, access to the building's roof is all that is required.
Ron Geren, FCSI Lifetime Member, AIA, CCS, CCCA, CSC, SCIP
Chad Hanley (Unregistered Guest)
Unregistered guest
Posted on Tuesday, September 01, 2020 - 04:50 pm:   Edit PostDelete PostPrint Post

Michael: Design team wants to avoid a ladder on the exterior of the penthouse, otherwise that would be the simpler solution.

Ron: That's a sensible description that I hadn't considered, fire department access into the building from the roof. I was thinking in the other direction, but your description makes more obvious sense. Thanks!
Marc Chavez
Senior Member
Username: mchavez

Post Number: 604
Registered: 07-2002
Posted on Tuesday, September 01, 2020 - 05:29 pm:   Edit PostDelete PostPrint Post

fun fact, on tall city buildings the City of Seattle requires stairs to the roof. no ladders. The hatch must tie to a stair, have an automatic opener from top and bottom and be heated for snow melt....$$$$$. got to love fire marshals. and as for the ladder maybe the design team could just go .:-) ...removed by internal sensor .... :-)