We have a jobsite situation where we need fire rated grout (above cmu wall/below metal deck) Have you ever used this grout? Who makes it?

I have checked with several major USA grout producers and found nothing. All I am finding is FP grout (with no psi on website) by Alibaba, and their site all goes thru China. I doubt they will reply to my question.

Have you ever needed FR grout?
George A. Everding, FCSI, CCS, CCCA, AIA
Senior Member
Username: geverding

Post Number: 813
Registered: 11-2004


Posted on Tuesday, November 10, 2015 - 03:55 pm:   Edit PostDelete PostPrint Post

Typically individual products by themselves do not carry a fire-resistance rating. They must be part of a tested assembly.

Why aren't you considering a fire-resistive joint system from the manufacturers listed in http://www.4specs.com/s/07/07-8400.html ?
Ronald L. Geren, FCSI, AIA, CCS, CCCA, SCIP
Senior Member
Username: specman

Post Number: 1363
Registered: 03-2003


Posted on Tuesday, November 10, 2015 - 10:28 pm:   Edit PostDelete PostPrint Post

Grout is cementitious, just like the rest of the CMU wall. There are no fire-rated grouts. If the full thickness is provided, then the grout has the same rating as the wall. It is similar to the exception for through penetrations.

However, there is a problem using grout for the joint condition you are describing--there is no bond between the grout and the metal deck. The metal deck will move, and any movement of the deck will break whatever bond there could possibly exist, allowing the passage of smoke and hot gases through the gap.

The joint should have some sealing capability like a standard joint sealant, whether the joint is static or dynamic. UL has a several head-of-wall assemblies designed for use with metal decks and CMU (usually as an option in lieu of CIP concrete walls) for gaps up to 6 inches, all of which are considered dynamic. However, the CMU, per UL, "shall bear the UL or ULc Certification Mark," which is problematic, since there are few manufacturers that have CMU with the UL Certification Mark.

Personally, I think requiring the mark for CMU is a UL racket (they do not require a certification mark for concrete materials in a concrete wall). Any CMU complying with ASTM C 90 should be acceptable. If there is any weakness in a fire-resistance-rated CMU wall, it will be in the mortar joints and not the CMU--and the mortar joint materials require no UL Certification Mark.

To overcome this obstacle, negotiations with the AHJ in the form of a code modification may be necessary by either requesting the use of non-UL-certified CMU or submitting an engineering judgement by the manufacturer of the joint materials indicating non-UL-certified materials are acceptable.
Ron Geren, FCSI, AIA, CCS, CCCA, SCIP
www.specsandcodes.com
Bruce Konschuh
Senior Member
Username: brucek

Post Number: 12
Registered: 08-2014
Posted on Thursday, November 12, 2015 - 05:21 pm:   Edit PostDelete PostPrint Post

Thanks for your thoughts re this issue. We went the route of "Grout is cementitious, just like the rest of the CMU wall. There are no fire-rated grouts."

There are a few FR mortars, but the psi was too low. Actually, the FR grout from Alibaba does meet the required 5000 psi, but I doubt the AHJ would have approved it.
Mark Gilligan SE,
Senior Member
Username: mark_gilligan

Post Number: 770
Registered: 10-2007
Posted on Thursday, November 12, 2015 - 09:55 pm:   Edit PostDelete PostPrint Post

I concur with Ronald regarding UL certification of CMU although I would be less polite.

The IBC provides a fire rating for CMU walls. I suggest you use this rating.
Dave Metzger
Senior Member
Username: davemetzger

Post Number: 613
Registered: 07-2001


Posted on Thursday, November 12, 2015 - 11:18 pm:   Edit PostDelete PostPrint Post

Alibaba is a distributor, not a manufacturer (sort of like Grainger but on a much larger, more wide-ranging scale)
John Bunzick, CCS, CCCA, LEED AP
Senior Member
Username: bunzick

Post Number: 1654
Registered: 03-2002
Posted on Sunday, November 15, 2015 - 06:02 pm:   Edit PostDelete PostPrint Post

Actually, Alibaba is more like Amazon, serving as an ecommerce portal for many companies selling products. They have several sites, including Taobao and Tmall. They are part-owned by Yahoo, and the founder, Jack Ma, is China's richest citizen, worth about $25 billion.